Federal Pacific main panel and circuit breakers

This kind of a FYI post.
Couple weeks ago we had a whole house generator installed and and new main electrical panel in our house.
The reason for the new main electrical panel was the original owner who built the house in 77-78 used Federal Pacific main panel and breakers.
We had three bids on the generator and all three electricians told us even if we don't do the generator the Federal Pacific stuff had to go. Serious issues with the breakers not tripping and catching the wires on fire. Google it its pretty scary.
So today we had a state inspector in to inspect the electrical work. He also confirmed the Federal Pacific stuff is a fire waiting to happen.
Again just FYI.
LS short box is offline   Reply With Quote
Old 05-15-2024, 10:12 AM   #2
MJN
Registered User
 
MJN's Avatar
 
Join Date: Feb 2000
Location: Maquoketa, Ia/ Orr, Mn
Posts: 2,972
Re: Federal Pacific main panel and circuit breakers

My first house had a FP panel and breakers. I got the same feedback when I bought the house and it got replaced in short order. Surprisingly the local hardware store still had breakers on the shelf for those panels.
__________________
'51 South Bend Model "9A"
'56 Chevy 3600 NAPCO
'74 Chevy Cheyenne Super K20-restored on 37's
'72 GMC Sierra Custom K2500- in progress
'08 GMC Envoy Denali
'12 GMC Sierra 2500HD Denali
'17 GMC Yukon XL
VCCA member #58596
http://www.nohrco.com
MJN is offline   Reply With Quote
Old 05-15-2024, 01:37 PM   #3
bnorth
Registered User
 
Join Date: Aug 2020
Location: Salmon Arm BC
Posts: 145
Re: Federal Pacific main panel and circuit breakers

We looked at a place to buy last summer built in the late 60's that had the FP setup and it was strongly recommended that it was replaced. Apparently failure rate on the breakers is in the 30% range where they don't trip.
__________________
1970 C10 l/b 292/4spd
Build: http://67-72chevytrucks.com/vboard/s...d.php?t=811062
bnorth is offline   Reply With Quote
Old 05-15-2024, 02:49 PM   #4
GOPAPA
"Tail Gate Best Seat In House"
 
GOPAPA's Avatar
 
Join Date: Oct 2007
Location: Nampa Idaho
Posts: 7,388
Re: Federal Pacific main panel and circuit breakers

I am surprised that they did not have a ground wire to the ground, even the old screw in fuse boxes I replaced had that.
__________________
When you learn a thing a day you store up smart.
GOPAPA is offline   Reply With Quote
Old 05-15-2024, 04:01 PM   #5
Dead Parrot
Registered User
 
Join Date: Aug 2012
Location: Oklahoma City, OK
Posts: 2,495
Re: Federal Pacific main panel and circuit breakers

Pretty much the same info was discussed on a welding forum I often read. My childhood home built in the late 60's had FP breakers. But we dodged the aluminum wire fiasco. All the wires were copper. No longer my problem, that house was sold in the late 80's.

But a good idea to replace if you have FP breakers.
Dead Parrot is offline   Reply With Quote
Old 05-15-2024, 05:31 PM   #6
richard2717
Equal opportunity joke ofender
 
richard2717's Avatar
 
Join Date: Oct 2011
Location: Eastern Shore of MD
Posts: 9,905
Re: Federal Pacific main panel and circuit breakers

I have been slowly changing out several aluminum wire circuits in my house. It was a mixture of aluminum and copper wire from the start and everything was backstabbed in the devices. I changed out all the devices when I first moved in to get rid of the backstab originals. Still have 2 rooms left with aluminum wire. Very seldom do they get used so no load on any of it. The FP panel was changed on day one with a Square D QO panel. The FP panel was actually in really good shape visually but I had already had a few stories of fires with them. The house was built in 74 I think.
__________________
Members I have met.
Dually Jams, OlBlue60, ScottH, Tommyboy24, Dujobo, Warbucket, 2003 Silverado, Notsolo, my90k5, 6t727t2, Special-K ,Jack_71C10, tabarcus,72blazer_mud_bogger,pwdcougar,RSavage,EricSean,1Rippen6,invicta455,tennaragtop71,arks, Kendal,Bennett68C10, Perpendicular, Chainsawman, McGeesCustomMinis,ShortbedClayton,longblue72,6768chevylover,Tim71,Travisarmenta,Ol' Drippy,fleetmitch,georgieb51,Dave,bcnya2,Dadsburb
https://paypal.me/6772GMtruckparts
Most women like the strong, silent type… Fortunately for me, my wife prefers the out-of-shape, mouthy type.
richard2717 is offline   Reply With Quote
Old 05-15-2024, 08:30 PM   #7
LS short box
Registered User
 
Join Date: Jun 2015
Location: Carlos MN
Posts: 1,943
Re: Federal Pacific main panel and circuit breakers

No alum wires in our house so just the main panel change out.
LS short box is offline   Reply With Quote
Old 05-15-2024, 10:41 PM   #8
Steeveedee
Who Changed This?
 
Steeveedee's Avatar
 
Join Date: Jan 2013
Location: Simi Valley, CA
Posts: 10,131
Re: Federal Pacific main panel and circuit breakers

Quote:
Originally Posted by richard2717 View Post
I have been slowly changing out several aluminum wire circuits in my house. It was a mixture of aluminum and copper wire from the start and everything was backstabbed in the devices. I changed out all the devices when I first moved in to get rid of the backstab originals. Still have 2 rooms left with aluminum wire. Very seldom do they get used so no load on any of it. The FP panel was changed on day one with a Square D QO panel. The FP panel was actually in really good shape visually but I had already had a few stories of fires with them. The house was built in 74 I think.
Not sure what "back-stabbed" means. When we bought this house (built in '68, so I knew it had aluminum wiring) I was told that there were "pigtails" installed. I pulled a switch plate to cover to check, and nope. The people who owned the place previous to us had been assured that the pigtails had been installed. They had been sold a bill of goods. They had to have pigtails installed before we bought it. In the process (which I observed), there was one outlet and one switch which had scorched wiring. Death waiting to happen.
__________________
~Steven

'70 Chevy 3/4T Longhorn CST 402/400/3.56 Custom Camper

Simi Valley, CA
Steeveedee is offline   Reply With Quote
Old 05-16-2024, 07:31 AM   #9
richard2717
Equal opportunity joke ofender
 
richard2717's Avatar
 
Join Date: Oct 2011
Location: Eastern Shore of MD
Posts: 9,905
Re: Federal Pacific main panel and circuit breakers

Quote:
Originally Posted by Steeveedee View Post
Not sure what "back-stabbed" means.
Pushing the wires into the back of the device instead of wrapping the wire around the screws on the side is called backstabbing around here. Was supposed to speed things up and the only thing I have ever seen it speed up is fire. I had to redo all of my parents devices as well after 2 small fires. Luckily no real damage happened in either instance. Backstabbing should have been outlawed a long time ago but they still make the devices with them.
__________________
Members I have met.
Dually Jams, OlBlue60, ScottH, Tommyboy24, Dujobo, Warbucket, 2003 Silverado, Notsolo, my90k5, 6t727t2, Special-K ,Jack_71C10, tabarcus,72blazer_mud_bogger,pwdcougar,RSavage,EricSean,1Rippen6,invicta455,tennaragtop71,arks, Kendal,Bennett68C10, Perpendicular, Chainsawman, McGeesCustomMinis,ShortbedClayton,longblue72,6768chevylover,Tim71,Travisarmenta,Ol' Drippy,fleetmitch,georgieb51,Dave,bcnya2,Dadsburb
https://paypal.me/6772GMtruckparts
Most women like the strong, silent type… Fortunately for me, my wife prefers the out-of-shape, mouthy type.
richard2717 is offline   Reply With Quote
Old 05-16-2024, 10:44 AM   #10
GOPAPA
"Tail Gate Best Seat In House"
 
GOPAPA's Avatar
 
Join Date: Oct 2007
Location: Nampa Idaho
Posts: 7,388
Re: Federal Pacific main panel and circuit breakers

Quote:
Originally Posted by richard2717 View Post
Pushing the wires into the back of the device instead of wrapping the wire around the screws on the side is called backstabbing around here. Was supposed to speed things up and the only thing I have ever seen it speed up is fire. I had to redo all of my parents devices as well after 2 small fires. Luckily no real damage happened in either instance. Backstabbing should have been outlawed a long time ago but they still make the devices with them.
Thx Richard for the expanation of back stabbing

I never knew the expression ,,but I never used the back side of any plugin or switch anyways to fasten my hot wire or primary wire ,, to loose a connection to suit me to put the face plate on call it good . I like a sure fit and the screw on the side is it.. dont mean to sound like a preacher,, just happy I never had a fire from the way I was taught to do it ,
__________________
When you learn a thing a day you store up smart.
GOPAPA is offline   Reply With Quote
Old 05-16-2024, 12:16 PM   #11
bnorth
Registered User
 
Join Date: Aug 2020
Location: Salmon Arm BC
Posts: 145
Re: Federal Pacific main panel and circuit breakers

Backstabbing is particularly bad with aluminum wiring due to the expansion/contraction of aluminum with heat and it's tendency to work its way out of the backstabbed connection. Hence why the fix is to pigtail the aluminum to copper for the connection to the outlet/switch. The wirenut connection on the aluminum to copper is much more secure with that heat cycling.
__________________
1970 C10 l/b 292/4spd
Build: http://67-72chevytrucks.com/vboard/s...d.php?t=811062
bnorth is offline   Reply With Quote
Old 05-16-2024, 05:10 PM   #12
old Rusty C10
Robert Olson Transport
 
old Rusty C10's Avatar
 
Join Date: Oct 2002
Location: recent transplant to NC USA
Posts: 20,273
Re: Federal Pacific main panel and circuit breakers

i am 60 and when i was a kid they lost their underwriters labratories certification because the breakers have aluminum and copper in them and weld. i personally had a house that was fully attached to mine back when i lived in NY and the house next door the Columbia University grad moron left for work with a hair dryer running and after the fire, I had $140,000 worth of damage but i could stand on what was left of my roof and see to her basement.. she had those FP breakers/ box
__________________
Bob



1951 International running on a squarebody chassis


"If a man's worth is judged by the people he associates himself with, then i am the richest man in the world knowing some of the fine people of this board"
http://67-72chevytrucks.com/vboard/a...t.php?f=25&a=9 (you can review the site rules here!)


PM Me for your vehicle/parts hauling needs in the North East US or see my Facebook page Robert Olson Transport

Live each day to the fullest.. you never know when fate is going to pull the rug out from under you...
I hate cancer!!
old Rusty C10 is offline   Reply With Quote
Old 05-16-2024, 07:02 PM   #13
dave6672
Senior Member
 
dave6672's Avatar
 
Join Date: Jul 2008
Location: Carrollton, KY
Posts: 1,177
Re: Federal Pacific main panel and circuit breakers

I take care of the maintenance at my church and when we were shopping for new insurance, one of the carriers told us that if we had any Federal Pacific Stab-Loc panels that they would not quote our insurance. I thought, "Oh, we don't have any of those". I went into the cellar to check the panels and sure enough, we have two of them. Something else to fix.
__________________
Dave R.

1972 K20
1972 C20 Highlander
1957 Chevy 210 Delray
1967 C10
dave6672 is offline   Reply With Quote
Old 05-16-2024, 11:03 PM   #14
Steeveedee
Who Changed This?
 
Steeveedee's Avatar
 
Join Date: Jan 2013
Location: Simi Valley, CA
Posts: 10,131
Re: Federal Pacific main panel and circuit breakers

Quote:
Originally Posted by richard2717 View Post
Pushing the wires into the back of the device instead of wrapping the wire around the screws on the side is called backstabbing around here. Was supposed to speed things up and the only thing I have ever seen it speed up is fire. I had to redo all of my parents devices as well after 2 small fires. Luckily no real damage happened in either instance. Backstabbing should have been outlawed a long time ago but they still make the devices with them.
Thanks for the explanation. I've always used the screws to attach wires to outlets and light switches. Just looking at those type of outlets, I dindn't like the looks of the spring connectors. Our current house was built with aluminum wiring, btu we had the pigtails retrofitted. I'll have to check the breaker panel when I get back home.
__________________
~Steven

'70 Chevy 3/4T Longhorn CST 402/400/3.56 Custom Camper

Simi Valley, CA
Steeveedee is offline   Reply With Quote
Old 05-18-2024, 11:00 PM   #15
joedoh
Senior Member
 
joedoh's Avatar
 
Join Date: May 2007
Location: Doodah Kansas
Posts: 7,748
Re: Federal Pacific main panel and circuit breakers

my current house had a fed pac box, failed inspection (but not the purchase), local company replaced the box and brought everything up to code, that was 2010 and it was about 14k to move the panel to the garage and upgrade a couple lines.

bought another place with a shop, city made me fix up the house to use the shop, another fed pac box and this time i took the local test (i am a double E with common sense and a code book) and did it all my self, main replacement, sub replacement, all new 4 wire 220 lines, GFCI bathrooms and kitchen, including the 100A copper feed to the shop. cost about 4k. I also at the time added an addition on our house and wired it too, 100A sub panel.

what astounded me about the house i live in that it was still a 40A drop from the 50s. 2400sq ft with elec stove and dryer. two aircon! I have no idea how it wasnt a flaming pile of wreckage.
__________________
the mass of men live lives of quiet desperation


if there is a problem, I can have it.

new project WAYNE http://67-72chevytrucks.com/vboard/s...d.php?t=844393
joedoh is offline   Reply With Quote
Reply

Bookmarks


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -4. The time now is 06:26 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Copyright 1997-2022 67-72chevytrucks.com